A big thank you goes out to Peter Argyropoulos of Petros Electric for sharing these photos with us. He found this installation in rural Pennsylvania.

According to Argyropoulos, “This service feeds a dwelling as well as a large mechanic’s shop where they do welding, tire replacements, etc. The female cord end sticking out of the disconnect box is the generator hookup. There is a suicide cord that the generator installer made for the hookup.”

Backfeeding an attachment plug in this manner is a violation of Sec. 406.7(B).  Prongs of attachment plugs must not be energized unless inserted into an energized receptacle or cord connector.

Argyropoulos adds, “The individual 2/0 aluminum feeders coming out of the white PVC at ground level, which enter the enclosure via separate ½-in. KOs, feed the mechanic’s shop.” These wires violate the requirements of Sec. 300.3(A) because single conductors must be installed in a Chapter 3 wiring method. They also violate Sec. 300.20(B), since no slots were cut between the individual openings.

“The issue I was called out for is that the generator breaker tripped every time they tried to connect it to power the house,” explains Argyropoulos. “I’d say the linemen were very lucky it did.” Section 702.5 requires transfer equipment to be used for this generator hookup.

Mauled at the Mall

Thanks also go out to Brian McElroy, a project supervisor for Elk Electric of Morgantown, W.V., for sharing this photo with us. He ran across this mess as part of a store remodel project in a strip mall.

According to McElroy, “This is a 3-phase non-fused disconnect. Only three conductors where used, but all six were live. There was no ground anywhere, and they had filled the EMT conduit with silicone. This also made the disconnect no longer waterproof.”

Section 300.18(A) requires raceways to be installed complete between outlets, junctions, or splicing points. This raceway was obviously not quite complete before this installation was made. Because this raceway came up a little short — and it was being used for equipment grounding purposes — it has compromised the continuity of the equipment grounding conductor. Section 300.10 requires metal raceways and metallic enclosures to be metallically joined together into one continuous electrical conductor and shall be connected in a manner to provide effective electrical continuity.

I also question whether there is enough space for all those wires crammed into the left side of the enclosure. Section 312.8 sets a limit for conductor fill to a maximum 40% of the cross-sectional area. This disconnect may be overcrowded.

About the Author

Russ LeBlanc

Russ LeBlanc

Owner

Russ started in the electrical trade as an apprentice in 1985. He worked his way up to become a Journeyman Electrician and then eventually became a Master Electrician and Licensed Construction Supervisor. In 1999 Russ become an Electrical Instructor for The Peterson School of Engineering in Massachusetts where he developed his passion for teaching, and quickly became Department Head of Electrical Instruction. Russ has taught thousands of apprentices, electricians, engineers, inspectors, and other electrical professionals during his career as an instructor. He continues to provide electrical professionals with Electrical Code seminars, Arc-Flash Awareness training seminars and educational material through his LeBlanc Consulting Services in North Reading, MA whose specialty is educating electricians. He has been an active member of the NFPA Electrical Section and has authored hundreds of National Electrical Code proposals and comments which have become Code rules to improve the safety for the electrical industry. Russ is also an IAEI certified Electrical Inspector.

Please visit www.russleblanc.net for more information.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!