Illustrated Catastrophes: A Less-Than-Weatherproof Installation

See the latest Code violations from NEC Consultant Russ LeBlanc.

All references are based on the 2023 edition of the NEC.

A Less-Than-Weatherproof Installation

I noticed this arrangement at the outdoor seating area for a restaurant while visiting an island off the coast of New England. From a distance, I could not tell whether the cable was UF cable or NM cable, so I got up close to take a better look and determined it was NM cable. Installing NM cables in wet locations like this one is prohibited by Sec. 334.12(B)(4).

The cable connector, used to secure the NM cable to the box, is not rated for use in a wet location either. As specified in Sec. 314.15, “Boxes, conduit bodies, outlet box hoods, and fittings installed in wet locations shall be listed for use in wet locations.” The box cover being crooked and leaving part of the box uncovered does not prevent moisture from entering or accumulating within the box as is required by Sec. 314.15.

On a more positive note, the luminaires are rated for wet locations and are also aimed horizontally or below as is required by the markings stamped on the side of each luminaire. The one lamp installed is also rated for this wet location.

Let Me Level With You

Like the Leaning Tower of Pisa, the conduits supporting this box are leaning quite a bit off-level. Conduits being unlevel is not necessarily a Code violation in and of itself. However, the length of the conduits emerging from the ground may be the reason they are leaning so much and does not comply with Sec. 314.23(E). That section does permit two rigid metal conduits threaded wrenchtight into a box no larger than 100 cu. in. with threaded entries or threaded hubs as the support for the box, but the conduits must be secured within 18 in. of the box if all the conduit entries are on the same side. This box is sitting approximately 2 ft above the ground, so it does not quite comply with Sec. 314.23(E).

If two or more conduits enter the box but are not entering the same side of the box, the conduit supports can be at 3 ft from the box instead of within 18 in. For using conduits to support boxes or enclosures containing devices, luminaires, or lampholders, installations must comply with Sec. 314.23(F) instead of Sec. 314.23(E). An easy solution here might be to install a 4-in. × 4-in. pressure-treated post, or something similar to support the box.

About the Author

Russ LeBlanc

Russ LeBlanc

Owner

Russ started in the electrical trade as an apprentice in 1985. He worked his way up to become a Journeyman Electrician and then eventually became a Master Electrician and Licensed Construction Supervisor. In 1999 Russ become an Electrical Instructor for The Peterson School of Engineering in Massachusetts where he developed his passion for teaching, and quickly became Department Head of Electrical Instruction. Russ has taught thousands of apprentices, electricians, engineers, inspectors, and other electrical professionals during his career as an instructor. He continues to provide electrical professionals with Electrical Code seminars, Arc-Flash Awareness training seminars and educational material through his LeBlanc Consulting Services in North Reading, MA whose specialty is educating electricians. He has been an active member of the NFPA Electrical Section and has authored hundreds of National Electrical Code proposals and comments which have become Code rules to improve the safety for the electrical industry. Russ is also an IAEI certified Electrical Inspector.

Please visit www.russleblanc.net for more information.

Sign up for our eNewsletters
Get the latest news and updates

Voice Your Opinion!