What’s Wrong Here? Hint: Bus Bar Peek-a-Boo
Do you know how this installation violates the NEC?
Hint: Bus bar peek-a-boo
The huge opening created by the missing circuit breaker blanks is large enough for a person to stick their entire hand in the enclosure and contact the energized bus bars. This is a real shock hazard and violates the requirements of Sec. 408.7. Unused circuit breaker openings must be closed with closures identified for that purpose or with some other approved means that provides protection substantially equivalent to the enclosure walls. Section 110.27(A) also has several requirements to prevent accidental contact with energized parts of electrical equipment operating at 50V through 1,000V, including using approved enclosures. Another concern with the missing breaker blanks is the increased probability of arcs and sparks escaping this enclosure and igniting nearby combustible materials.
Russ LeBlanc
Russ LeBlanc