What’s Wrong Here? Hint: Suspicious Supporting Methods
Hint: Suspicious supporting methods.
I am not so sure that securing Electrical Metallic Tubing (EMT) to a water pipe satisfies the intent of Sec. 358.30. Should the EMT be supported to the structure instead? I believe that is the intent, however the wording in Sec. 358.30 only requires the EMT to be “securely fastened in place” without actually stating that it must be secured to the structure. Perhaps if the water pipe is independently securely fastened in place too this method might be ok with the AHJ. Of course, if the raceways are being used to support the water pipe, then that would violate Sec. 300.13(C).
Another concern I have with this installation is the “home made” transition fitting installed between the EMT and the LFMC raceways. Using EMT connectors and LFMC connectors with a threaded RMC coupling may be a violation of Sec. 110.3(B) if that coupling is not designed and listed for use with connectors having straight threads. Typically, conduit fittings having internal (female) threads are listed for use with the tapered threads on metal conduits. Listed transition fittings are available for various wiring method transitions.
Russ LeBlancRuss LeBlanc