What’s Wrong Here? Hint: Wrong Raceway Fittings
Hint: Wrong raceway fittings.
Set screw EMT couplings were not the correct choice of fittings for this rooftop raceway installation. Where fittings are installed in wet locations such as this, Sec. 358.42(2) requires the use of fittings listed for use in wet locations. This type of set screw coupling is not listed for use in wet locations. Compression type fittings would have been a better choice here. Also, the separated raceway sections create a violation of Sec. 300.12 which requires metal raceways to be metallically joined together and connected to all metal boxes, fittings, and cabinets to form a continuous electrical conductor that provides an effective ground fault current path. In addition, it appears that this EMT is not properly supported and secured in accordance with Sec. 358.30.
Russ LeBlancRuss LeBlanc