What’s Wrong Here? Hint: Get the Raceway Stretcher
Hint: Get the raceway stretcher
For general applications, Sec. 300.12 requires raceways, cable armor, and cable sheaths to be continuous between boxes, fittings, cabinets, and other enclosures. This electrical metallic tubing (EMT) raceway came up a little short. Exception No. 1 allows short sections of raceways to provide support or protection of cables without requiring the raceway to be mechanically continuous. Exception No. 2 allows raceway and cables entering the bottom of open bottom enclosures such as switchboards, motor control centers, and pad-mounted transformers without the cables or raceways being secured to the equipment. Neither of those exceptions apply here. Single insulated conductors as specified in Table 310.104(A) are only permitted when installed in wiring methods recognized in Chapter 3. The transition fitting and connector used to secure the cables are designed for use with NM cables. Using fittings or connectors with wiring methods other than for what they are designed and listed is a violation of Sec. 300.15 and Sec. 110.3(B).
Russ LeBlanc
Russ LeBlanc